New Build Inspections Snagging Service
Home arrow New Homes News
Snagging Shop
Make sure you find all
the defects in your
new home. Purchase
our snagging guide.
Snagging Guide
Reviews
Get a professional
snagger to create a
snag list for your new
property in the UK or Ireland.
Snagging Inspections
Want more rights?
writetothem.com
Main Menu
Home
New Homes News
Snagging Stories
New Homes Research
Snagging Forum
Snagging Cloud
Snagging Top Ten
Web Links
Snagging Photos
Property Books
Online Shop
Polls
Directory
Press
 
Login for Download
Contact us
 
Site Map
New Build Inspections
The leading truly independent snagging company.

UK: Snagging
Ireland: Snag List


 

Go Back   Snagging.org Forum > Developers > Persimmon Homes

Reply
 
LinkBack Thread Tools Display Modes
  #11 (permalink)  
Old 4th March 2008, 17:30
Junior Member
 
Join Date: Jan 2008
Posts: 17
katherineparkvictim2
Default Re:Persimmon Fit Undersized Radiators

Persimmon have agreed to move the upstairs thermostat, but we still haven't received any radiator information from them - have given them a nudge today!

Can't wait to hear how you got on with the NHBC regarding the water logged garage walls!
Reply With Quote
  #12 (permalink)  
Old 19th March 2008, 17:07
Junior Member
 
Join Date: Aug 2007
Posts: 5
liz69
Default Re:Persimmon Fit Undersized Radiators

katherineparkvictim can you post the formula you used to work out the heating output needed to heat a room?

We have a Persimmon built home on a different development and are having problems with the largest bedroom not heating up properly. We think another radiator needs to be fitted in there as it's a simillar size room to the lounge which has 2 radiators and this room heats up really well.

Also katherineparkvictim2 you mention you had British Gas round to assess your situation, is this a general free service they offer that anyone can request or is it for customers only?

I am trying to get any documents regarding radiators from Persimmons (obviously it's a slow process). If the plans do show that there should be only one radiator in the bedroom could you dispute this and say that the plans are flawed?

Liz
Reply With Quote
  #13 (permalink)  
Old 20th March 2008, 19:12
Junior Member
 
Join Date: Jan 2008
Posts: 17
katherineparkvictim2
Default Re:Persimmon Fit Undersized Radiators

Hi Liz,

We have a breakdown policy with British Gas and, as part of this, they offer to do an energy efficiency analysis for free. We didn't know this when we booked them to do the survey, but are pleased it was!

The Engineer measured two of the rooms and then calculated the KW's needed to heat the room. Because there are no markings on the radiators, it was impossible for him to say if they are big enough or not, but looking at them, he didn't think they are.

Persimmon have refused to issue us with the radiator schedule from Domestic Heating Design in Kettering, saying it's not company policy. We phoned them direct and they wouldn't give them to us, saying Persimmon wouldn't allow it. However, Persimmon have arranged for a Senior Engineer from PSS Midlands to come and survey the house, which he did yesterday afternoon. He has measured all the radiators in cms and is now going to go away and work out if they're big enough or not. He says generally, whatever the schedule says, the plumber 'knocks off 10% of the upstairs radiator sizes', based on the theory that heat rises, so they don't need to be so big.

He also agreed that the thermostat is incorrectly positioned and we discussed where to re-site it, but I said the two coldest bedrooms (can't get them above 17 degrees) needed bigger radiators first.

If your house plan showed two radiators in the bedroom, then they should either have fitted two, or one big enough to have the correct KW output. If they haven't followed the schedule then you can certainly get them to correct it.

Also, you most certainly can dispute the fact that your house is not heating up correctly, the Engineer from British Gas said they're well known for skimping on radiators and he gets call outs all the time. He had to come and 'balance' our heating and did in fact disable some of the radiator thermostats to 'force' the heating to work better. It has improved, but does mean the boiler is not working at optimum capacity etc.

If I were you, I'd get British Gas round to assess your heating, or insist that Persimmon send PSS round, and pursue the issue fervently!

Good luck!
Reply With Quote
  #14 (permalink)  
Old 22nd March 2008, 13:07
Junior Member
 
Join Date: Aug 2007
Posts: 5
liz69
Default Re:Persimmon Fit Undersized Radiators

Thanks for your reply katherineparkvictim2.

I shall look into getting British Gas round, but who are PSS?

We also got the same blurb that the upstairs will always be colder than downstairs, but the way things are I'm sure the garage is warmer than the bedroom!

Also is there any chance that Persimmon would turn around and say we have invalidated any guarantees by getting an independant round? I know I'm being overly cautious but after hearing some of the ridiculous things that have come from Persimmons, anything is possible with them.

I would be interested to know how you get on with this issue, so keep us updated (I'll do the same if I have any luck)

Good luck to you too!

Liz.
Reply With Quote
  #15 (permalink)  
Old 31st March 2008, 20:37
Junior Member
 
Join Date: Jan 2008
Posts: 17
katherineparkvictim2
Default Re:Persimmon Fit Undersized Radiators

Hi Liz, PSS Midlands are the independent plumbing company that Persimmon have called in, although I believe Renelec actually plumbed the system in here.

I think the only way you could invalidate a guarantee with Persimmon is if you were to go ahead and have another contractor make some alterations, but just inspecting it is not changing anything, so they can't possibly object - especially as we had British Gas round!

We're still waiting for PSS to report back, but I will let you know what they say.
Reply With Quote
  #16 (permalink)  
Old 2nd April 2008, 01:00
Junior Member
 
Join Date: Oct 2007
Posts: 15
KatherineParkVictim
Default Re:Persimmon Fit Undersized Radiators

Apologies for not posting back sooner, but a lot has gone on. We’ll do a quick response now on events, and answer the queries in your posts, but will come back by the end of the week with more detail – just want you to know we’re all on the same lines:

Update: Our NHBC visit on 4 March was a good result – the NHBC inspector looked at the Persimmon Radiator Schedule (from DHD), the DeLonghi catalogue for the compact radiators specified and fitted, spotted the shortfall – and then (we love this bit) turned to persimmon’s man and stated “But this is obvious!”. I was chewing on my knuckle to stifle the laughter at this. Wonderful.

NHBC then tasked Persimmon formally to account for the difference – the response from DHD in a nutshell (and buried under paragraphs of techno babble) said ‘Run your boiler central heating water temp at 80 degrees C’ – in English they’re saying that if you run them hotter, the undersized rads will provide enough output. This higher setting, they state, is agreed with the Persimmon group. That looks like they have bounced the issue back to Persimmon.

The problem with this is that we, the customer, are being told to run the boiler hotter than it is designed for – the manufacturer’s setting for design efficiency is 70 degrees C, and has been confirmed by Glow Worm as such for our boiler.

This means Persimmon, with their decision to fit smaller radiators (saving costs up-front) want us, their customers, to run inefficient boiler settings, burn more fuel, bigger bills, and of course a bigger carbon footprint, etc – right against what common sense and the government are saying should be the case. Our independent has confirmed our thoughts on the inefficiency, etc.

We will now be going back to NHBC with this as our response, and are looking at engaging such bodies as might well take a significant media interest in Persimmon’s (undisclosed) policy on this. We have also engaged a consultant who is standing by to produce a court admissible report – he’s a specialist and does this a lot, so we’re covered if/when this goes to court (and it will if it needs to, we promise you).

From your posts:

Radiator Schedule - They cannot withhold the radiator schedule – company policy or not – as you should be given this under the Freedom of Information Act; it relates directly to you and your affairs, nor is it commercially sensitive information, etc - and as such is a prime candidate for consideration under this act. Suggest you contact your MP if they do not comply.

If any Katherine Park Phase 1 Richmond house type owners want sight of our DHD radiator schedule, we would be happy to let you have a copy - it details the plots covered; see my earlier posts. The DeLonghi catologue is also very hard to source, but we will happily share that with you as well (as it specifies exactly the radiator type and all technical information). Just send us a separate message, and it will be taken care of.

Independents – Completely agree on what has been said, we gave a copy of our indeps’ radiator report to NHBC in front of Persimmon, and there was no problem – it was actually quoted in the NHBC response to persimmon as well – worth its weight in gold!

Heating Formula – We initially used the Persimmon schedule and DeLonghi’s radiator catalogue, but our independent did a load of calculations and came to the same conclusion in his written report. Most heating engineers have an industry recognised bit of software that works it out and generates a calculation sheet on all the factors – we wouldn’t do this ourselves, but covered it through the independent to also gain more authority.
:cheer:
Reply With Quote
  #17 (permalink)  
Old 4th April 2008, 15:11
Junior Member
 
Join Date: Mar 2008
Posts: 8
togo.bevan
Default Re:Persimmon Fit Undersized Radiators

Hi

I am also interested in this one as I have been trying to get a copy of our property drawings at assess the U-values.

How is the Freedom of Information Act applicable to Persimmon / NHBC as they are not regarded as public bodies?
Reply With Quote
  #18 (permalink)  
Old 7th April 2008, 14:13
Junior Member
 
Join Date: Jan 2008
Posts: 17
katherineparkvictim2
Default Re:Persimmon Fit Undersized Radiators

Hi, I got copies of the house drawings from the Council, but they were as vague as the ones in their sales brochure. I don't understand why they can withhold the information, but they are. We've just had a Building Surveyor in on another matter and he also says they should give us all our drawings etc, but I don't know how to make them do it. A solicitor's letter?

I've just chased Persimmon today for the outcome of the inspection on 19th March. We had thought the heating would soon be going off, but now it's gone cold again, so the issue is back in the forefront of our minds. Will keep you posted...
Reply With Quote
  #19 (permalink)  
Old 22nd May 2008, 14:57
Junior Member
 
Join Date: Jan 2008
Posts: 17
katherineparkvictim2
Default Re:Persimmon Fit Undersized Radiators

Well, here we are a month later, still waiting for the Renelec report on our heating. He totally agreed that the two rooms upstairs are much colder than the rest, easily felt on a cold day without the need for a thermometer. Everyone has agreed the room thermostat needs to be relocated from the airing cupboard wall to another wall, but we're still no further forward regarding the radiators. Apparently the ones fitted are DeLonghi Compacts, so it shouldn't be too difficult to work out the KW's/room size etc. But, I resent having to do this work, as I think Renelec should have to do it. Will let you know when/if they ever respond! Frustrated Berkeley Owner!
Reply With Quote
  #20 (permalink)  
Old 23rd May 2008, 08:29
Member
 
Join Date: Jan 2007
Posts: 55
Warwick
Default Re:Persimmon Fit Undersized Radiators

Read the report very carefully, but I would take the oppertunity to work out the sizes and then inform NHBC
Reply With Quote
Reply

Bookmarks

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT +1. The time now is 05:12.


Powered by vBulletin® Version 3.7.1
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Content Relevant URLs by vBSEO 3.1.0